Lag Screw into End Grain of a 2x8???

Lag Screw into End Grain of a 2x8???

Lag Screw into End Grain of a 2x8???

(OP)

I’m looking into possibly requiring the installation of a ½” diameter lag screw into the end grain of a 2x8.

Obviously I have several concerns regarding this:

1.  Constructability:  I’m concerned that when the lead holes for the lag screws are drilled, the contractor will damage the 2x8.  Would requiring an epoxy screw help to mitigate any damage?

2.  Has anybody had experience with this type of connection?

RE: Lag Screw into End Grain of a 2x8???

Smitty9898,

How is the lag being loaded?  Attaching into end grain should be avoided.  For either shear or withdrawl the NDS provides a cooresponding C(eg) factor (end grain factor)

Jordan

RE: Lag Screw into End Grain of a 2x8???

(OP)
The lag screw is being used to attach a 2x12 ledger flush against the ends of 2x8's.

The withdraw load on the anchor is approximately 80 pounds, the shear load is approximately 100 pounds.  I'm also installing masonry epoxy bolts for the ledger, which will take some of the shear load.

RE: Lag Screw into End Grain of a 2x8???

The NDS code does address combination shear and withdrawl loading Z for lags into endgrain.

Jordan

RE: Lag Screw into End Grain of a 2x8???

(OP)
Woodengineer,

Thanks for the response!  Do you know what section (or page#), addresses the combination shear/withdrawl into endgrain?

Any experience with epoxy bolts into wood?  Do you think it would be a more durable connection, as compared to a lag screw?

RE: Lag Screw into End Grain of a 2x8???

For the NDS 2001 it is found in Appendix J (NON-MANDATORY) solution of Hankinson Formula, Page 161.

Ceg = 0.67 into end grain.  For a lag bolt in end grain Fem=Fe(perp)

I have no experience with epoxy bolts into wood.  Check with the manufacturer rather than creating a solution.

Good luck!

Jordan

RE: Lag Screw into End Grain of a 2x8???

I may not be picturing the connection correctly, but how about blocking between the 2x8s and attaching the 2x12 ledger to the blocking?  Better connections.  I'd avoid end-grain lagging if at all possible.

RE: Lag Screw into End Grain of a 2x8???

How about inverted joist hangers for the the 2x12 ledger connection to the 2x8 ends?

I also would recommend, avoid lagging to the end grain if possible.

RE: Lag Screw into End Grain of a 2x8???

The inverted joist hangers is better than my idea but www.socketsystems.com sell pre-drilled purlin clips that are a 1/8th or so thick steel angle with predrilled holes.

I'm using them to attach a fascia to cantalevered 2x6's so it can be installed from the roof (difficult to get to the face of the overhang, 26 ft above ground on a hill).

RE: Lag Screw into End Grain of a 2x8???

Past experience, try to avoid fastening into end grain. Not a good idea.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources