Does Halon detection system works with FM200

Does Halon detection system works with FM200

Does Halon detection system works with FM200

(OP)
Could someone please tell me, is it possible to maintain fire detection system (i.e  fire control panel, detectors) used in halon system to be reused with FM200 system.

your help will be appreciated.

RE: Does Halon detection system works with FM200

I believe that so long as the panel is listed for releasing service and the realeasing mechanisms are compatible with the clean agent cylinders and panel your OK. Your switching from halon to FM 200 so you will need to confirm compatibility of the fire alarm control panel with the control modules installed on the cylinders for agent release.

Based on your post I'm assuming you have verified compatibility of the nozzles for the selected hazard and design conditions and appropriate pipe sizing for your hazard?

I need to check NFPA 72 and 2001 tomorrow, and I will do that in the AM before I can offer a concrete answer. Sorry I can't do it any earlier.

RE: Does Halon detection system works with FM200

(OP)
how can I verified that Fire Control Panel/Detectors are compatible with the clean agent release? could you please explian?

thanks

RE: Does Halon detection system works with FM200

You may be able to use the detectors if they are compatible with (UL and FM listed) to be used with new FM200 control panel. The new FM200 system supplier will not accept/warranty the new system with old control panel. So althogh theoratically possible, do not use the existing control panel with a new releasing system as it will not be listed for use with FM200 solenoid.

It all comes down to liability and not so much as to technical.


RE: Does Halon detection system works with FM200

look in the panel or call the maker to see if the panel is listed for release. In the panel you should see one of many ul stickers and if listed for release there will be s sticker saying it.


http://database.ul.com/cgi-bin/XYV/template/LISCANADA/1FRAME/showpage.html?name=SYZVC.GuideInfo&;ccnshorttitle=Control+Units,+Releasing+Device+Service&objid=1076372312&cfgid=1073741824&;version=versionless&parent_id=1076372311&sequence=1

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources