galvanic isolation of pole guying

galvanic isolation of pole guying

galvanic isolation of pole guying

(OP)
In thread238-162891 advidana mentioned that "an insulator is required on the guy line from the pole to the ground for galvanic protection"

What sort of a configuration requires that?

We require insulator in guys, but I was told is was so that if the top part becomes accidently energized, the public cannot walk up and touch a hot ground wire.  Also it allows workers on the pole a measure of safety if they touch something hot and the top of the guy wire.  Some utilities do the opposite, requiring everything thing to be grounded so the relaying will operate faster, especially in areas where the soil is poor.

RE: galvanic isolation of pole guying

The usual reason for a guy insulator is as you noted, for safety if the top of the guy is in the primary area.  A fiberglass rod guy insulator is also often used to increase pole top BIL.  If the guy is bonded to the neutral and the neutral is grounded separately with a copper ground rod, then galvanic corrosion will be likely. The galvanized anchor rod and anchor will be a sacrificial anode to the copper ground rod.  A guy insulator will prevent galvanic currents from flowing.

RE: galvanic isolation of pole guying

Thank jghist for good explaination on the use of the guy insulator.

RE: galvanic isolation of pole guying

Use of a guy insulator will reduce, but not prevent, galvanic currents.  If there are disimilar metals like galvanized anchor and copper ground wire, the galvanic action can take place in low resistivity soils, even if the two metals are not bonded together.  The use of galvanized ground wire and rods with galvanized anchor rods is one solution.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources