How to size a UPS for 60 hp, 480 3 ph motor?
Been asked to determine a budget cost to provide a UPS feed motor as listed above. Never sized a unit of this size before so not sure where to start. Any suggestions / thoughts would be nice.
RE: How to size a UPS for 60 hp, 480 3 ph motor?
You need to get the UPS manufacturer's recommendation. At minimum consider a solit state reduced voltage starter or a VFD, this will help a great deal to keep the UPS size within limits.
I'd talk it over with two or three UPS vendors. And write your spec to explain **precisely** what the UPS is required to do. Try to shift as much of the risk to the supplier as possible. If you just order a UPS and it doesn't work, it will be your problem. If you write a performance spec, the UPS supplier will be responsible for making it work.
You also need to backup any controls so the motor doesn't get stopped by the start input when the power goes out.
Some manufacturers may be able to supply a battery back-up system as described by LionelHutz above.
Third part accessory suppliers may also be able to supply a battery back-up system. One is http://www.bonitron.com/. There may be others.
If it's a VFD you could possibly set back the motor's speed 10% or so to extend the battery run.
100A @ 600V
(100)6V batteries deep cycles.
Keith Cress
All great suggestions - just wish it would be a standard option from a drive manufacture.
I once came up with engineering on a list of options available for a VFD manufacturer using a lot of the custom projects I had worked on prior to coming to work for them. They offered them and nobody bought a single one, mostly because their version needed to be slightly different than mine anyway, which made it an engineered special anyway.
http:/www.jraef.com
Eng-Tips: Help for your job, not for your homework Read FAQ731-376