Transformer Inrush:

Is there a detailed standard method for calculating max transformer inrush current (initial starting inrush) during energizing a transformer? I know that the x/r is dynamic and that the inrush depends on when in time the transformer is energized relative to the residual flux residing in the core.

Capacitor Outrush:

Is there a method for calculating the max capacitor outrush current during a fault. Is is the same as the inrush current?

Inrush current = 1.2*root(2)*v(line-ground)*root(C/L)?

RE: Transformer Initial Inrush Current and Capacitor Fault Outrush Current

In reality, trasformer magnetizing inrush current will depend heavily on core saturation (you can’t model it with linear L/R model).

Just guessing on cap current (not sure)
Cap current assuming cap terminals are shorted to ground.
I guess there is assumed some internal resistance to limit current?
Then v(t)=V0*exp(-t/RC)   where we might take V0 as peak value of line to ground voltage.
i(t) = C * dv/dt = -C*V0/(RC)  * V0*exp(-t/RC)  
i(t) = -V0/R  * V0*exp(-t/RC)  

I suspect due to the high frequency nature of the transient of shorting terminals, inductance might play a role as well.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Transformer Initial Inrush Current and Capacitor Fault Outrush Current

The peak outrush current during a fault would be determined by the same equation as in the OP except that the inductance L would be the inductance of the line between the capacitor and the fault instead of the system inductance.

RE: Transformer Initial Inrush Current and Capacitor Fault Outrush Current

If you have access to Cooper Power System "Electrical Distribution-System Protection" Book (3rd ed.) p.104, will address this subject. (Capacitor Out-Rush Current) It does not reveal calculations, but does recommend expulsion fuse/current limiting devices to use.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources