flow / velovity measurement

flow / velovity measurement

flow / velovity measurement

(OP)
We are trying to get away from discrete alarming on Exhaust flow.  We have considered a number of options with analog transmitters, but I thought that I would through the this out there to see if anyone had any ideas / reccomendations.

the 2 meters I am presently looking at most are Dwyer:
http://www.dwyer-inst.com/htdocs/PDFFILES/cat/airvelocity/641_cat.pdf


http://www.dwyer-inst.com/htdocs/airvelocity/SeriesAVUSpec.CFM


as well as one from E+E Eleoctronics

RE: flow / velovity measurement

(OP)
Oh yeah, some of the applications are somewhat dirty, and acidic

RE: flow / velovity measurement

What is the purpose of getting away from discreet alarming? If you use an analog signal you will still have to set a limit at which the airflow is unacceptable. Unless you need a specific airflow reading at your monitoring station?? If this is the case, I would choose the 4-20ma output instrument, especially if the distance is long between the instrument and the analog input card.

RE: flow / velovity measurement

(OP)
yes, the Dwyer are 4-20, but they are 3/4 wire, and we want 2 wire.  

We are a heavily regulated facility, and it has been stated that more precice SPs are required, and that exhausts will eventuall be mandated to have totalisers.  

RE: flow / velovity measurement

Review the exhaust conditions i.e. temperature, pressure and chemical composition. As with most regulated process you need to report SCFM * time to get to total CFM. The Dwyer probe you are looking at is for clean dry air at atmosphic pressure and is a single point in the air stream.  I recommend the use of a permanent flow monitor flow grid in the exhaust duct. I have used
  http://www.airmonitor.com/documents/process/brochures/BRO_LOflo_SS_12503800.pdf#search='Flow%20measuring%20station'

http://www.kele.com/olcat/F5/kms.pdf

You can get custom sizes. You need to determine the system accuracy and do a very good initial calibration that is traceable.

Take the delta p output to a transmitter with 4-20ma or 0-10v output. Various mfgs offer complete solutions with local display. It sounds like you are trying to reuse the existing 2 wire alarm system. If the wiring is your problem, you may want to look into a wireless solution.

http://www.kele.com/tech/monitor/Flow/TRAirFlw.html

http://www.lambdasquare.com/

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources