(OP)
In the designing of Water Storage tank, is there a rule or method of determining if its necessary, to use columns and rafters?. I have a Tank with 16 feet x 23 feet and a conical "self supported" roof of 3/16" thick, and a Tan 20º of slope.


         Thanks.

RE: Rafters and Columns Required.

API-650 gives a formula for thickness of a self-supporting cone roof as t = D/(400 sin(theta)), where theta is the slope angle.  With your tank dimensions, a self-supporting cone roof of 3/16" would work okay.  This assumes dead+snow load of 45 PSF or less.

This equation is in API-650 but is commonly applied to AWWA tanks as well.  It can generally be shown that roofs meeting this requirement will comply with the compressive stress formulas of AWWA as well.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources