ground wire in multi core cable

ground wire in multi core cable

ground wire in multi core cable

(OP)
Hello,

Are there any tables in the NEC (or equivalent) that specify the minimum size of the ground wire in a multicore cable?  

For example, what ground wire size would be used in a #2, 3C, 5kV cable?

Thanks for the help!

RE: ground wire in multi core cable

The ground wire size is based on the upstream overcurrent protection rating, not the phase conductor size.  See Table 250.122.

RE: ground wire in multi core cable

Table 250.122 may be a reference but 250.180 is for ckts of 1kv and higher. Check 250.190.

RE: ground wire in multi core cable

You might wish to verify what common cable ground sizes are available in a multi conductor assembly. No matter what you calculate or determine per code table, if it isn't manufactured, you will have difficulty sourcing it.

RE: ground wire in multi core cable

In the cables that I have installed over the years, the ground conductor was usually adequate for equipment grounding, but was often inadequate for system grounding or common grounding.
You must check the cable specs. for the actual size of the ground conductor and then check the code to see if it is adequate for the intended application. You may have to instal an additional ground conductor alongside the cable.
respectfully

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources