Variable Volume and Temperature (VVT) system sizing.
What happens to a VVT system if the zone boxes are oversized for acoustical sound reasons?  Will the system be controlable?
RE: Variable Volume and Temperature (VVT) system sizing.
Suggest you post to the HVAC/R Engineering forum.
Depends on how much they are oversized.  This is a damper control with reheat - Flow will present the most issues.  If the required flow is say only 25% of the capacity you will end up with real issues trying to get controllable airflows and space temps, at 75% it will probably work, or at least most of the time.
I recommend using a correctly sized box, as they typically all are capable of meeting reasonable specs (say NC35) and treating the noise as it's own mech/arch problem - Choice of box manufacturer, Acoustic rated ceiling tiles, lead-impregnated vinyl sheets around boxes, full height partitions, insulating boxes...
It can be aproblem if they are sized too large. The modulating damper could act like a two position damper instead. Barely open could provide full flow for example.
The HVAC forum might be more helpful as mentioned above.
Ed
www.engineerboards.com