What happens to a VVT system if the zone boxes are oversized for acoustical sound reasons? Will the system be controlable?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Variable Volume and Temperature (VVT) system sizing.
|
RE: Variable Volume and Temperature (VVT) system sizing.
Depends on how much they are oversized. This is a damper control with reheat - Flow will present the most issues. If the required flow is say only 25% of the capacity you will end up with real issues trying to get controllable airflows and space temps, at 75% it will probably work, or at least most of the time.
I recommend using a correctly sized box, as they typically all are capable of meeting reasonable specs (say NC35) and treating the noise as it's own mech/arch problem - Choice of box manufacturer, Acoustic rated ceiling tiles, lead-impregnated vinyl sheets around boxes, full height partitions, insulating boxes...
RE: Variable Volume and Temperature (VVT) system sizing.
The HVAC forum might be more helpful as mentioned above.