Generator slash rating

Generator slash rating

Generator slash rating

(OP)
I have seen a generator rating as 60/75 kva or 75/60 kva. The smaller number is referring the overload rating of the generator. My question is "Is there a standard convention”.

RE: Generator slash rating

What else you read on the generator?

Voltage, frequency, power factor, rpm??
Standby/ Prime?

I suspect it is meant say 60kW/75kvA and 0.8 power factor

75kvA * .8 pf = 60kW.

Or it could be prime rating (lower value) and stand-by rating (higher value). But usually prime rating is 10% lower than the standby rating.


RE: Generator slash rating

I agree completely rbulsara.
respectfully

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources