is a standard breaker (sq.D FAL) instantaneous trip?

is a standard breaker (sq.D FAL) instantaneous trip?

is a standard breaker (sq.D FAL) instantaneous trip?

(OP)
I am considering using a breaker for a motor short-circuit and  ground-fault protection (standard thermal-magnetic sq.d FAL series) as per NEC 430.52.

I'm not sure if this is classified as an instantaneous trip or an inverse-time breaker. I downloaded the trip curves, but its not clear exactly what category it would fall into.

thanks in advance! Its for determining the current rating based on 250%/800% of motor FLA.

RE: is a standard breaker (sq.D FAL) instantaneous trip?

A thermal-mag breaker has both inverse time and instantaneous trip.

A "mag-only" or motor-circuit protector is a molded-case breaker with no thermal (inverse time) trip.  

RE: is a standard breaker (sq.D FAL) instantaneous trip?

(OP)
well, I guess my question is, how is it classified as per code?

RE: is a standard breaker (sq.D FAL) instantaneous trip?

bio:

Both. Since it has inverse time (thermal) characteristics which comes in play during motor starting current, its rating shall be selected as permitted for inverse time breakers. It is this characteristics that permit a smaller size (ampere rating) breaker for a motor breakr compared to one with only instaneous (magnetic) element. Make sure If adjustable, the instantaneous trip is set to high,

The instaneous (magentic) part provides short circuit protection as required by code.

Speaking of plotting curves, you make sure that you also load the motor curve. The breaker curve shall remain to right and above the motor current curve and the breaker rating shall not exceed what Code permits. That is all you need to confirm.

Beyond that sit down with an electrical engineer friend who knows the subject.



RE: is a standard breaker (sq.D FAL) instantaneous trip?

Careful, the FAL can come in either format, depending on the catalog number.

The only caveat to all this is that the Mag (Instantaneous) trips on a Thermal-Mag breaker are fixed at the factory in that frame size, not adjustable. It's sometimes tricky to get the right continuous amp rating while still staying within the allowable limits of the NEC 430.52 sizing (including exceptions). In some motor applications, especially when starting ATL (DOL), the magnetization inrush may exceed that fixed rating and cause nuisance tripping. That's why MCPs are used in motor circuits as a rule, they have higher trip ranges and adjustability to avoid nuisance tripping on motor inrush.

http:/www.jraef.com
Eng-Tips: Help for your job, not for your homework  Read FAQ731-376 pirate

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources