Fan Sizing for Room Pressurization

Fan Sizing for Room Pressurization

Fan Sizing for Room Pressurization

(OP)
Just need a sanity check. When sizing an air handler for a room that is to be pressurized, I must add that pressure to the fan external static, correct?  In other words, let's say that my duct and other external losses amount to 3"W.C.  Let's also say that I want to pressurize the room to 0.25"W.C. (pretty high, but just as an example).  When selecting the AHU, I will need to tell the manufacturer that I need so many CFM @ 3.25"W.C. external static - correct?

RE: Fan Sizing for Room Pressurization

It's the "so many CFM" that you really need to think about; you need to calculate (amongst other things) how much air will be leaking out of the pressurised room at 0.25" Aq.

Brian

RE: Fan Sizing for Room Pressurization

Yes, you're right BronYrAur, although it's usually negligible compared to the other losses in the duct serving the room...

RE: Fan Sizing for Room Pressurization

Yes. That is correct and if you really want 0.25" wc (this is generally high) it is prudent to include in fan ESP.

I have a personalized opinion here. Most of the times, we tend to be redundant in duct design. Ex. rounding up to nearest even number, high roughness factor, future requirement and FOS. In this cases, you are already running your fan to the right of the design point and 0.25", if not considered initially, will help you to get the operating point to the left a bit.

After all, it is your own judgement.

RE: Fan Sizing for Room Pressurization

(OP)
Thanks everyone.  I just used 0.25" as an example to drive home the point.  I have never had the need to pressurize anywhere close to that.

RE: Fan Sizing for Room Pressurization

I am currently designing some stairwell pressurization systems.  I plan to use relief dampers to control the upper limit of pressurization.  Ie.. when the stair tower reaches .25" the relief damper opens and limits it to that upper set point.  For my application, this is to stay within the allowable pressure range dictated by IBC, which is .15" to .35".  I will also have to consider stack effect in the tower as well during both design summer and design winter conditions.

Jabba

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources