Commissioning of dampers
Commissioning of dampers
(OP)
Is actual commissioning of fire, F/S and smoke dampers involve whether they close w/o binding or is it just installation checks such as for sleeve clearance, breakaway connections, access doors, etc?





RE: Commissioning of dampers
Fire, ceiling, and smoke dampers should be installed in accordance with the manufacturers’ instructions. NFPA Standard 90A gives general guidelines regarding locations requiring these dampers. ASHRAE handbook 2003 applications section A52
RE: Commissioning of dampers
RE: Commissioning of dampers
cme,
The fire damper testing is destructive in nature (unless it is electronically activated by smoke or temperature sensors). I didn't check NFPA (as it is not relevant at my place) but all fusible link dampers are type tested and have the certificate with you as an installation check point.
RE: Commissioning of dampers
For Fire Dampers with Fusible Link, insist on UL Certified Fusible Links.
For Dampers with actuators, use a Control Panel, which will permit you to check Damper Operation via the panel (Closing and Opening for Spring Return Actuators).
Finally, source Dampers from a manufacturer who has had his dampers type tested at a competent facility for conformance to UL555 standards.