SHUNT TRIP FOR SERVICE DISCONNECT

SHUNT TRIP FOR SERVICE DISCONNECT

SHUNT TRIP FOR SERVICE DISCONNECT

(OP)
NEED AN OUTDOOR SERVICE DISCONNECT FOR 1600A, 480V SERVICE WITH (6)-4" UNDERGROUND CONDUITS (25FT TOTAL LENGTH)FEEDING A MOTOR CONTROL CENTER JUST INSIDE BLDG FROM A 13.2KV/480V XFMR JUST OUTSIDE THE BLDG. SHORT OF A 1600A, 480V BREAKER OUTSIDE WOULD A SHUNT TRIP COIL ON THE MCC MAIN BREAKER AND A PUSHBUTTON MOUNTED TO THE BLDG EXTERIOR WALL BE AN ACCEPTABLE SERVICE DISCONNECT ?

RE: SHUNT TRIP FOR SERVICE DISCONNECT

Not to me it wouldn't.  The pushbutton is not a service disconnecting means per NEC definition.  It can't be locked open to prevent someone from closing the breaker back in.  And the shunt trip requires a source of control power to function.  

Who's telling you the disconnect has to be outside?

(Ron - find the Caps Lock key on your computer and give it a little punch looking around)

RE: SHUNT TRIP FOR SERVICE DISCONNECT

The outdoor service disconnet will be your code required service disconnect. The shunt-trip you mention is not prohibited for emergency stop but it will not be considered a servcie disconnect. You don't have to have the service disconnet inside the building. Where is your metering?

Why do you need the push-button? Emergenc power off? If you want to work on the MCC safely, only acceptable method is to lock out the outdoor switch.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.