criteria for selecting a switchgear?
Apart from the obvious, what other criteria it is necessary to account for the selection of switchgears? i.e operationability, etc tec
sac
sac
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
criteria for selecting a switchgear?criteria for selecting a switchgear?(OP)
sac Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
RE: criteria for selecting a switchgear?
http
David Baird
Sr Controls Designer
EET degree.
Journeyman Electrician.
thanks
In most cases, all of these manufacturers will meet your requirements as per manufacturing standard (IEC or ANSI). The common denominator in most cases will be the overall cost (material + delivery) and the delivery time (as dictated by your commisioning date as well as warranty and spare parts availability.
It is not proper to compare each one of them as per make since all of them are having common denominators as well in the design and manufacture of these equipment.
Design and set your parameters and check their offered specs.
GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata
All three can meet minimum specs but workability can vary widely. Also, try to get a factory visit if you can.
http:/www.jraef.com
Eng-Tips: Help for your job, not for your homework Read FAQ731-376
I don't know if these are 'apart from the obvious' or not, but here are a few, anyway...
1. Interruption medium: Gas or Vacuum? What's the state of the art? What gives you the interrupting ratings that you need. Do all three on your list of suppliers offer both?
2. Insulation medium: gas or air?
3. The answers from (1) & (2) lead to maintenance and monitoring. Does the customer deserve the added grief of gas monitoring and topping off? Also, life expectancy and actual or simulated aging of the interrupters would most likely be the customer's No.1 question.
4. Space. How much room do you have? Have you drawn your oneline and added all necessary magnetics to achieve your protection and metering goals and asked the three manufacturers for their layout?. This is very important because brand 'A' for example is limited to say six CT's per breaker, wheras brand 'B, can install twelve. The same applies for PT's. The differences in size must be accounted for in your real estate.
5. Further to your oneline, you need to tell the manufacturers where are your cables entering and exiting the equipment top, bottom, side, and have them include that in their layout to see how large the equipment gets.
6. What auxiliary equipment is needed for installing the circuit breakers in place, what auxiliary equipment is required for moving the circuit breakers in the electrical romm? Do the breakers roll in and out on their own, or do you need some attachments? What does the customer prefer? Do you have space for storage of all that equipment?
7. Can the breakers be easily tested via switchgear built-in features, or do you need special equipment? That must be factored in the initial cost.
8. What maneuvering (sp?) is required to erect the equipment: forklifts, cranes, rollers, skates, other? Does your installation offer whatever the suppliers require?
9. How accessible are the instrument compartments for maintenance and troubleshooting? Do you need a six foot ladder to climb in and reach?
10. Are the bus joints in the main circuit and cable terminations easy to insulate? Are they applying removable boots, or do they require taping? Factor that in your installation cost.
11. Who provides the longest terminating distances for your MV cables? Does that match your terminators?
And the list goes on and on. But finally, please be advised that, worldwide, there are other manufacturers than the ones you've listed - some here in the USA.
The other aspects as described by iigp2006 dictates that you should fully do your basic designs and consideration and the vendors will try build them.
I can offer you some basic suggestions but you have to provide me the application of your switchgear: Voltage, Type of Load to Feed and whether you are installing this to an existing building or a newly designed substation.
