AB Micrologix 1000 questions
Its been years since I've done an AB PLC, last ones were way back in time with the SLC500 bricks.
Client *insisted* on a Micrologix.  OK, so I now have a Micrologix1000, and gettng RSLOGIX updated to do the programming.  I have a model 1761-L32AWA
Looking thru the manual, and googling some haven't come up with the comm port info.  All I see is a single mini-DIN connector on top, next to the status lights.  I assume this is the programming port, but is it DH+, DH485, what? I need to tie a panelview into this PLC as well, so do I use that same port?
Also, is this PLC expandable? I think so, most are, but again I dont see an expansion port.
Anyone familiar with these?
RE: AB Micrologix 1000 questions
thanks for the link to the other group.  I did a search for micrologix before I posted and ended up empty.
The port is an RS-232 DF1 full duplex port, if that is any assistance.
  I don't suffer from insanity. I enjoy it...
Did you ever get an answer to your question? Try Pub. # 1761-6.3 from this link:                                 http://literature.rockwellautomation.com/idc/groups/public/documents/webassets/browse_results.hcst?lineTitle=MicroLogix1000%20System&familyTitle=Programmable%20Logic%20Controllers&categoryTitle=Programmable%20Controllers&;xLanguage=EN%20-%20English&CategoryId=0012&FamilyId=0088&passedLangVal=EN%20-%20English
Do a copy paste. Also AIC #1761-Net-AIC will allow you to connect DH-485, which is Panelview friendly. Also, Rslinx can help with the communication problems. Good luck.
Your best bet is to call your local Rockwell supplier that sold you the PLC.  They usually have a tech onsite that can help get you going.  Sometimes they'll come onsite to help out if you're in jam - especially if you are a customer that purchases alot of equipment!
True...used to do alot of AB but then went to a less expensive brand till this.  I'm not sure if our local guys have much knowledge, but worth a try.
I just thought at least the documentation that came with it ought to have a little more explantion of the comm ports.
The link provided in the prior posting was helpful in that it did tell me I can't add an 10/100 module because there is no way to expand the I/O (good) and the port is RS232, so now I know what panelview interface to order.
Thanks folks