Insulation- Question on Cladding
In a thermal insulation system, we normally use Aluminium cladding to protect. When installing the cladding, are there any requirements or standards on which type of securing method to use? I prefer screw type instead of rivet, as I believe the maintenance fitters can fix them back more easily, and thus giving less excuses.
---engineering your life---
RE: Insulation- Question on Cladding
Seams on the bottom for a typical clamshell with SS straps and no need for rivets or screws.  If an odd geometry, then caulk the penetrations regardless if rivets or screws.
gramp, I'm not familiar with the method you suggested. But it appears that the securing is done through straps only? Will that be secure enough?
Here are some guidlines I'm familiar with:
Jacketing over insulation, for cylindrical surfaces 30 inches diameter and smaller, shall be secured with 1/2-inch by 0.020-inch bands and seals placed at 12-inch centers, maximum, over each circumferential overlap and at least at the center of each course of jacketing.
Jacketing for cylindrical surfaces greater than 30 inches diameter shall be secured with 3/4- inch by 0.020-inch bands and seals placed on 12-inch centers.  As a minimum, bands and seals shall be placed over each circumferential overlap and at least at the center of each course of jacketing.  In addition to the bands, longitudinal joints in jacketing shall be secured with sheet metal screws or pop rivets placed on 6-inch centers as required to avoid gaps in the jacketing.
Jacketing shall be applied with 2-inch circumferential or longitudinal laps as applicable.
Sheet metal screws or pop rivets shall not bind adjacent courses of jacketing together at the circumferential lap.
All overlaps in metal jacketing which are not installed in a watershed fashion, such as longitudinal seams in vertical piping and circumferential seams in horizontal piping, shall be sealed with caulking compound.
The straps are amazingly secure. They look like the pipe straps you use on flex duct, like on your dryer. It is usually a god idea to caulk the seams as well when doing this. Especially if it is exposed to the elements. IF the ductwork is outside, I have also seen the insulating company add another layer over the seam and strap it down with two (2) straps and caulk it so there is no problem or worry about potential leaks at the seams, it is protected.
Look at CINI Manual: Insulation For Industries
Steve Jones
http://www.pdo.co.om/pdo/