WIND LOAD ON TANKS
WIND LOAD ON TANKS
Hi, we are designing a Storage Tank under API STD 650, but we dont have very clear how to calculate the wind moment as its described in 3.11. Anything would be apreciated.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: WIND LOAD ON TANKS
Consider an example:
Suppose you have 85 mph 3-second gust, with a tank that is 24' high, 40' diameter.
The lateral wind pressure on the tank shell is 18 PSF x (85/120)^2 = 9.03 PSF. The overturning moment due to that wind pressure is 9.03 PSF x 40' x 24' x 12' to centroid = 104,026 ft-lbs.
The lateral wind pressure on the projected roof area is neglected, per a note there in Addendum 4.
The uplift pressure on the roof is 30 PSF x (85/120)^2 = 15.05 PSF. The uplift force is 15.05 PSF x pi/4 x 40^2 = 18,915 lbs. The moment arm for that force is the tank radius, so the moment is 18,915 ft-lbs x 20' = 378,300 ft-lbs.
Then total overturning moment is 104,026 ft-lbs + 378,300 ft-lbs = 482,326 ft-lbs.
Does that help?
You can compensate for ladders, piping, or stairways in the projected area if you need to.