Condensate pump design
Hello:
I have a steam condensate drum operating at 50 psig. I have designed a pump for this system where the destination pressure is also 50 psig. The discharge losses are around 30 psi (includes line pressure drop, exchanger and a control valve).
Should I design the pump for a differential pressure of 30 psi or 80 psi (to cater to a cold start up when the drum pressure may be very low). If I design for 80 psi delta, the pump will not operate near its best operating point during normal operations.
Is there a way out of this situation?
Thanks.
Thanks.
RE: Condensate pump design
For a cold startup, can you get rid of the condensate some way until you are up to normal (or close to it) operating pressures?
I'm not a real engineer, but I play one on T.V.
A.J. Gest, York Int./JCI
you can also add an expansion vessel connected to the suction with a pressure (above the diaphragm) of 50 psig.
regards,
roker