discharge coefecient of fire sprinklers

discharge coefecient of fire sprinklers

discharge coefecient of fire sprinklers

(OP)
What is the discharge (K) coefecient to be used on the typical fire sprinklers. The simulation will be carried out for metric units.

rgds

RE: discharge coefecient of fire sprinklers

The K factor for a sprinkler depends on what you specify, they are used as the major pressure drop in the system usually so that the flow is specific for each sprinkler and piping pressure drops do not significantly starve flow to furthest away components. As usch there is no such thing as a typical K factor, you specify what pressure you will supply by doing a firewater network flow calc and specify the flow you need in that area then buy the required K factor sprinkler.

RE: discharge coefecient of fire sprinklers

the k-factor is a constant value. it will depend on the maker and the orifice size.
typical k-factors for commerial heads
orifice        US    (metric)
1/2"..........k=5.6 (80)
17/32"........k=8.0 (115)
7/16".........k=4.2 (60)
3/8"..........k=2.8 (40)
10mm..........k=4.2 (60)
15mm..........k=5.6 (80)
20mm..........k=8.0 (115)


there are many makers and styles of sprinklers you should find some catalogs (on line) and they will be most helpful. some design specific heads require a minimum flow from the sprinker.

flow = (k)(square root of pressure)

just what is it you are trying to do?

hope this helps

G3

RE: discharge coefecient of fire sprinklers

Good information, PipeDream.  By the way, love your handle!

Kenneth J Hueston, PEng
Principal
Sturni-Hueston Engineering Inc
Edmonton, Alberta Canada

RE: discharge coefecient of fire sprinklers

Typically, in most office type buildings you will have 5.6K sprinklers.  When you have storage densities between 0.20 gpm / sq ft and .34 gpm / sq ft, you must use a minimum 8.0K sprinkler.  In storage areas with densities of >0.34, then you are required to use a sprinkler with a minimum of 11.2K.

There are many other variables that come into play when selecting the K-Factor for sprinklers.

RE: discharge coefecient of fire sprinklers

Additionally some of the fire sprinkler designs for high pile storage are based on a minimum starting pressure at a given K factor. So if your exercise is to attempt to select a sprinkler based on its K factor, you'll need to factor this also.

OK, I'll bite: What is the purpose of the simulation?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources