RCD and 0.75kw motor?

RCD and 0.75kw motor?

RCD and 0.75kw motor?

(OP)
Hi all

I am using a single phase TEC 0.75kw motor on 240v 50Hz UK supply.

every time we drop the supply to the motor the 30mA RCD trips?

I know motors can be electrically noisey, but is there a simpler way around this apart from upping the RCD to say 100mA??

Does anyone know where TEC motor are made? URL?

thanks

Dave

RE: RCD and 0.75kw motor?

Hi Dave
   We supply TEC motors...mainly the three phase though, because they are a CHINESE made motor, and we find that the chinese have not yet perfected the manufacture of capacitors, and have a rather heavy failure rate!
   As for the RCD tripping.....have you carried out an earth test on the motor, and if so, what readings are you getting?
                regards
                 Jeff
         www.motors-direct.co.uk

   

RE: RCD and 0.75kw motor?

Dave; It is not noise, it is "leakage" that is tripping your RCD (if RCD means ground fault protection). Your motor's insulation may be failing.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: RCD and 0.75kw motor?

(OP)
many thanks guys,

Jeff,

I did carry out IR test, 800 meg ohm.

Do you have URL for TEC?

thanks

Dave

RE: RCD and 0.75kw motor?

(OP)
we also noticed that the new TEC we had in was now wound differently to the one we evaluated.

Which surprised us! The connections are different in the motor terminals.

Same 0.75kw spec / chassis

?

Dave

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources