Can earth ground be tied to a common ground from a DC power supply?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
earth ground and Common ground!
|
earth ground and Common ground!earth ground and Common ground!(OP)
Can earth ground be tied to a common ground from a DC power supply?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: earth ground and Common ground!
Sometimes it would be better that way, sometimes it would not. (Because of noise paths.)
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: earth ground and Common ground!
It is usual for electrical systems to be earthed at some point rather than to be "floating". It is generally safer to earth internal supplies rather than let them float with respect to the mains supply.
Consider this: if a transformer is connected to mains on one side and the other side is left floating, what is the voltage stress applied to the insulation? If the output potential floats it may eventually over-stress the insulation on the transformer. Not good.
If there is more than one mains related earth in any system then you get into "earth loops". These can be very bad as they give noise/hum/stray currents. Handling earth loops correctly is an activity which many engineers spend much of their working lives coming to terms with.
RE: earth ground and Common ground!
Hello itsmoked/logbook
Since you answered the OPs question I would like to jump in with another.
If for example a large transformer is placed opposite side
of building from switch gear and the Electrician uses the
metal ceiling beams for ground connection on that transformer.
How does he know this is a good enough path? Can you use VOM
from ceiling light hot to beam and verify current flow, or
is there a NEC required procedure for this? Megger reading perhaps?
Chuck
A government which robs Peter to pay Paul
can always depend on the support of Paul.
- George Bernard Shaw
RE: earth ground and Common ground!
Basically this is a heavily regulated area and I wouldn't be comfortable recommending this action. There may well be all sorts of rules which make it illegal, but I can't specifically name any clause just yet. Typcially you might do an earth resistance check on the dead system using a simple multimeter and really long leads, initially doing an ohm-zero on the test leads. This would be necessary but no where near sufficient.
RE: earth ground and Common ground!
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: earth ground and Common ground!
and ask about it. These guy's are really good to have
around and it's possible I don't see some significant
connection somewhere.
Beside that he's like you Kieth if I hit he'll whoop the tar
out of me!
Chuck
A government which robs Peter to pay Paul
can always depend on the support of Paul.
- George Bernard Shaw
RE: earth ground and Common ground!
Thanks
respectfully
RE: earth ground and Common ground!
And...I'll be danged.. Better hold off whacking your sparky machmech. You can use steel building framing for grounding. It must be well connected. (bolted or welded I would imagine) This is similar to using water piping which is allowed.
However it seems you must "bond" the transformers to the building frame. I don't believe bolting the transformer to the frame cuts it, since mounting bolts don't specifically guarantee a good bond.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: earth ground and Common ground!
was grounded to frame and from there to ceiling we
have 5 hooked up this way through out building The
sparkys scrape the paint off beam or joist and bolt
a wire lug to it. In addition the conduit serves as
ground also.
Now at switch gear we have ground from gear to very
large water main and from there to ceiling. Outside
on main transformer several grounding rods where
installed, I think more then normal due to sandy
soil, not sure did not ask. Ground rods and water
pipe are roughly 8 feet apart.
So now I wonder if the potential for a ground loop
condition does exist under these circumstances.
I would think that water main will take care of
any stray current.
Yes I know some days I should just quit thinking!
Thank's Keith, Chuck
A government which robs Peter to pay Paul
can always depend on the support of Paul.
- George Bernard Shaw
RE: earth ground and Common ground!
This does not eliminate the need for an equipment grounding conductor in the incoming feeder to the transformer primary. This could be a green ground wire or metal conduit.
Under normal conditions, these are non-current carrying conductors.