Developing Fault Scenarios

Developing Fault Scenarios

Developing Fault Scenarios

(OP)
I am currently developing a list of fault scenarios for an arc flash study with a system containing over 500 busses and am wondering what the standard for developing these scenarios is? ie: Do I consider a fault at each and every bus for each operating configuration (tie breakers closed, tied breakers open) or do I only consider certian busses? If so, which busses should I be consider in developing the fault scenarios?

RE: Developing Fault Scenarios

You should be using a software package designed for the purpose.  Such software can evaluate all busses for any configuration of the system you select.  You need to look at configurations at both ends of the fault current range, sometimes a lower fault current provides a worse arc flash hazard than a higher fault current.

RE: Developing Fault Scenarios

(OP)
"sometimes a lower fault current provides a worse arc flash hazard than a higher fault current" - Can you elaborate on this? In what instances would this occur?

RE: Developing Fault Scenarios

Arc energy is a function of (among other things), fault current and fault duration.  In some cases, a slight reduction in fault current can result in dramatically longer fault duration - such as when an overcurrent relay or circuit breaker transitions from an instantaneous trip element to an inverse time trip element.  For a decrease of a few hundred amps of fault current, the clearing time may increase from 5 cycles to 5 seconds or longer.  This results in much higher arc-flash energy for the lower fault current.

If you don't have a copy of IEEE-1584, you should get one and review the step-by-step procedure outlined in it.  That will be a good starting point.

Then you will have to decide what scenarios you need to consider.  But it's not an exact science.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources