Static Excitation Pt. 5: Compound Boost CT revisited

Static Excitation Pt. 5: Compound Boost CT revisited

Static Excitation Pt. 5: Compound Boost CT revisited

(OP)
Hi, i managed to obtain some information about a special wound CT used in a compound-source static excitation system. There was a 'nameplate' located on the back of the CT, which in turn was directed to the wall. It seems the wound CT has one primary and 2 secondary coils. The primary has 3 windings, the secondary 19 & 3. The secondary coils are connected in series in a 'delta' way. As CT's are current sources, isn't it illegal to connect two current sources in series?

Can someone explain to me why the secondaries are connected to each other in this way. Maybe it has something to do with fault currents etc?

RE: Static Excitation Pt. 5: Compound Boost CT revisited

(OP)
Just got a stroke of genius: it looks like a weird kind of zigzag or interconnected wye connection.

This is my interpretation of it:

RE: Static Excitation Pt. 5: Compound Boost CT revisited

(OP)
I've read that the zigzag winding is used for absorbing triple-N harmonics, but doesn't the secondaries have to be symmetrical? What is the effect of 2 asymmetrical secondaries?

(PS: I hate it when you can't edit your own threads)






RE: Static Excitation Pt. 5: Compound Boost CT revisited

(OP)
After reading a PDF, i was finally able to assign a vector group to the CT. The primary side has vector group Y0, and the secondary Z7uw. 0-7=-7 or +5 phase shift (150 degrees) --> Yzn5



Another PDF mentions the following:
"Taking no special measures, following connection modes amount to 100% load of neutral point:
Delta-star connection with secondary extended neutral point Dy5
Star-zigzag connection with secondary extended neutral point Yz5
If three-phase sets are formed via 3 single-phase transformers, then load of neutral point must definitely be avoided"

Is this 'neutral loading' of any significance of the CT in relation to the exciter?


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources