Directional earth fault relay maloperation

Directional earth fault relay maloperation

Directional earth fault relay maloperation

(OP)
Directional earthfault relay receives VT input from the VT in the switchgear incomer cable box and CT input from that in the transformer neutral-to-earth connection. The relay is set to look away from the transformer.

Now, can some one tell me - whether the VT location is the reference for the directionality or the CT location? I think it is the CT location.

RE: Directional earth fault relay maloperation

Polarity determines the direction.

RE: Directional earth fault relay maloperation

The phase angle difference between the zero-sequence voltage measured by the VTs and the zero-sequence current measured by the CT is what determines the direction.  So, it takes both, with proper polarity, to have directionality.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources