Effects of Harmonics in Circuit Breakers

Effects of Harmonics in Circuit Breakers

Effects of Harmonics in Circuit Breakers

(OP)
I am installing new VSD's and motors on a crane that was originally built in 1965.  I have been able to estimate that under the worst case conditions the current THD will be approximatly 35% (which will be virtually un noticable to the rest of the plant).  However we are retaining some of the existing 400V electrical distribution equipement, including the 300A main circuit breaker.  My client wants to know if the CB will be affected by the harmonics, (5th about 29%, 7th 14% etc).  Any suggestions or comments would be appreciated.

RE: Effects of Harmonics in Circuit Breakers

Thermal-magnetic circuit breakers are true RMS devices and are not affected by harmonics. These types of breakers respond to the total heat and magnetic force generated by all current flowing through them.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources