Rupture disc calculation
I need to calculate if a 1 inch rupture disc at 15 psig will be satisfactory for a 150 gallon tank. The two scenarios include: negligible liquid and nearly all vapor or a nearly full tank with liquid. The nozzle on the vessel is 1/2" and a reducer is used to increase the pipe size to 1 inch prior to the rupture disk. The manufacturer of the rupture disk states that Kr=2.40. The rupture disk piping ties into a header which then goes to atmospheric pressure. Can someone shed some light on this issue?
RE: Rupture disc calculation
The flow is going to be determined by the 1/2" nozzle on the vessel.
You need to calculate the relief load and then the required orfice area. If the area is larger than the 1/2" nozzle you are in trouble.
Look at the Crosby engineering handbook for the loading calcuations. Look at one of the rupturedisk sites for how to incorporate a Kr factor into your orfice calculation.
StoneCold
Thanks for your help!
Good luck,
Latexman
Dan
The crosby book is free. Here is the link. I think if you read it it will help you a lot with this problem.
www.tycoflowcontrol-na.com/ld/CROMC-0296-US.pdf
If after reading the book you still have questions come back and I will try to help you more.
StoneCold
What you have identified in your original post as being "The two scenarios" is really only partial descriptions of the operating conditions of your tank. Generally speaking, a "scenario" would be in reference to an event that causes the pressure in your system to increase and if the event can exceed the maximum allowable pressure of any component within the system you are trying to protect, then it becomes an overpressure scenario for which you need to provide overpressure protection.
Determining the relief load requires you to have a good understanding of the processes involved that are affecting the system pressure. For example, if your tank is provided with a nitrogen purge system then failure or mis-operation of the nitrogen controls to the tank can cause the tank to overpressure. If so, then you would need to provide overpressure protection equal to the rate of nitrogen that was causing the overpessure. Overfilling the tank by pumping material into the tank is another common case to consider as is external fire resulting in heat input that could cause liquid vapor pressure to increase and eventually boil generating vapor that must be relieved.
This are to name only a few of the possible sources of overpressure. Since you are talking about a rupture disc set at 15 psig, I assume you have a pressure vessel so you should consider the code requirements for overpressure protection of the system (see this thread for additional info thread1203-157530).
The Crosby Handbook is a very good reference and it does include some discussion about how to determine a fire relief load. For more thorough coverage about how to determine your required relief rate, I would suggest you get a copy of API RP-521.
Also, here's a link to a good online resource discussing considerations for rupture discs...
http://www.cheresources.com/asiseeit.shtml
In addition to the important issues raised in the previous posts, don't forget to study the issue of process dynamics (instantaneous loads can be a lot higher than the steady-state or design value). Believe it or not, I have seen cases where the dynamic load exceeded the "maximum" steady-state value by over 25%. Such systems can be analyzed readily using currently available dynamic simulation software and studying the effects of worst-case jumps in the independent variables.
For information on everything you can learn on Rupture Discs, go to:
Phil Leckner puts on a show there that is top-notch in know-how and experience regarding safety devices - and it's all free.