How do I determine busbar junction resistance?
I am looking for advice on determining 'tyupical' busbar junction resistances.  My applications run up to 50kADC.  Usually minor losses aren't critical to me, but sometimes I need to be able to estimate what's going to happen every 12 feet when I bolt all that copper together.  Any advice?
Paul Matejcek
RE: How do I determine busbar junction resistance?
The copper development assosiation (UK) www.cda.org.uk publishes a publication "copper for busbars", which contains information on that topic.
For a good connection (suitable area, flat, free of oxide and bolted with hardware giving the right force in the whole temperature range) the loss is usually negliable.
electricuwe,
Thanks for the lead.  I didn't find that document on the US CDA page.  I briefly browsed the article on joints at the UK site, and it looks as though it will be helpful.
Paul Matejcek
Maybe I misunderstood the question, but measuring joint resistance requires a Kelvin connection.  First, a DC current is passed through the joint with one pair of leads.  [Microohmmeter are available with up to a 500-ampere test current, so the leads may need to be fat.]  Then, the voltage drop is measured with a second set of leads [with small AWG] connected to a (milli)voltmeter.  Then: R=V/I, making sure the decimal point is in the right place.  Simply, if precisely 1 ampere is passed, the each measured millivolt equates to 1 milliohm.
busbar,
Thanks -- I understand Ohm's Law, and how to get the data empirically.  My questions was about predicting the resistance.  Based on what I have learned today, it seems not to matter, because a well-made overlap joint (the sort I'm using) has a lower resistance than a similar length of bus.
Thanks again,
Paul Matejcek
Very simple!
Run  100Amps DC from a current generator and read the voltage drop on the contact. The higher the temperature the higher the drop voltage.
That means  resistance is not constant!!!
Traian
Paul - I agree that measurement is not relevant since we now understand your interest is in predicting junction resistance.
But I wanted to mention that Busbar's point was not simply a statement of ohm's law. He was explaining the 4-wire resistance measurement principle which almost entirely eliminates errors from lead resistance and probe contact resistance. Simple resistance measurements with 2-lead multimeter/ohmmeter are not nearly as accurate when measuring low resistances. Also a good discussion by Traian.
Thanks to all who have replied.  What I have subsequently learned probably should have been intuitively obvious: a properly made overlap joint has less resistance per unit length than the bus it joins.  A well-made joint is 'better' than a continuous run of bus.
Paul