utility power source 380/220 vac, 3 phase, wyn 50 hz with neutral. Question-is the neutral normally grounded in countries outside of the USA, such as the middle east for this type of power.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: 50 hz systems
The Middle East has inherited the 380/220 V TN-C and it is very common. But there might be exceptions.
Consult http://kropla.com/electric2.htm and similar sites for more information.
Gunnar Englund
www.gke.org
RE: 50 hz systems
RE: 50 hz systems
You're correct on the middle east, and at least one exception being Saudi. Last time I was there, they were still using 220/127V 60Hz.
A little gee-whiz FYI...
http://kropla.com/electric2.htm
Eric
RE: 50 hz systems
RE: 50 hz systems
To complete the answer to your question, you should be advised that in USA and Canada the most commom low voltage distribution level is 208/120 V, 60 Hz. The utility provides for each of their residential customers two phases and a neutral, and the residential wiring is designed such as the appliances are to be fed phase-to-phase (208 V) while the rest of the receptacles are phase-to-neutral (120 V).