Diesel Leak rate through a buried pipe
I need to calculate the rate diesel would leak out of a 2" steel pipe buried 3' below grade.  The hole was approx. 1/4" diameter and the pipe is under 20 psi pressure.  I know the soil type will probably affect the rate.  If it is easier, can I find the maximum leak rate assuming the pipe were not buried and then deal with how the pipe burial would affect the rate?
RE: Diesel Leak rate through a buried pipe
Are you trying to figure out how big a spill you have?
"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
No, not exactly.  I will figure that out with geological magic.  I am trying to figure out at what rate diesel could have leaked from the pipe.  An opposing consultant made an estimate and I am trying to check if their calculation is at all accurate.
I would think not just soil type, but soil compactness and density would also matter.
Also, the orientation of the hole may have an effect. Not sure how, but it may.
Albert Einstein
That is why I am starting with trying to find the leak rate without considering that it is buried.  Assume the worst case scenario would be the pipe leaking onto the surface.
Assuming that the ratio of the hole size 1/4" to 2" (2" Sch.40 pipe has ID of about 2"), the flow going out the leak would be about 1.5% of the original flow rate.
If you assume the soil conditions outside the pipe will further retard that, by let say 80% (pure guess here), then the  total leakage rate is 0.3% of the original total flow rate.
That's my unqualified off the top of my head guess.
What was the other consultant's number?
Albert Einstein
Well, if you use darcy law of diffusion thorough the porous structure to calculate the flow rate of the diesel through the buried pipe.
Hopefully it will give you valid approach and better results.
See the below link for detail:
http://biosystems.okstate.edu/darcy/LaLoi/basics.htm
I think with 20 psi, soil type would only be a factor for about a couple of minutes.  Even very dense compaction is going to give way to the jetting action, especially a leak as big as 1/4 inch.
I was thinking actually of a longer period of time, after a pool forms. I thought maybe the pool will dampen the jetting action, and the pipe will just be leading into the pool, and hence, affected by the "backpressure" of the pool.
Maybe like areas with a lot of clays?
Albert Einstein
Any oil under 20 psi is not going to let soil resistance stop it until you get way down to 30 feet or more and the pipe was drilled into a solid clay.
Just figure your leak rate without the soil.
I would agree with BI. Certainly the "full leak" is the number to work with.
Keith Cress
CarlB.  People seem to be confusing this with geological formations thousands of feet below surface where earth resistance is 8000+ psi.  20 lbs is a lot of force on a in3 of soil that is probably only 3 or 4 feet below ground surface level.  Most soil particles, especially in a usually poorly compacted backfilled pipeline trench with broken rock, some gravel, soil and sand around the pipe will be compressed into adjacent void spaces and will easily yield a flow path allowing fluid to go wherever it wants to go.  As soon as a grain of soil anywhere near the hole in the pipe tries to stop flow, flow backing up to the high pressure source brings the full pipeline pressure to bare to give it that extra needed little boost.  I can tell you... (as sure as the Space Shuttle can fly) it doesn't take long for it to just go straight up.  Later it may make its way down to an aquifer, but much much later.
You may be correct, but I think people are more likely visualizing what happens when a water jet strikes the ground surface dislodging unconfined particles.  Maybe someone will dig a 3 feet deep hole, bury the end of a garden hose, backfill and compact, let er rip, and see how long until it becomes a fountain.
Ha!  I was going to suggest they do the exact the same thing.
The reference you found seems to suggest that well compacted backfill is used over pipelines, which in general is very far from the truth.  While it may be true at specific constructions in city street works and rural highway undercrossings, I can assure you that it is absolutely not the case for the thousands of miles of oil pipelines making their cross-country runs as they try to avoid those areas where extra care in backfilling is demanded by public works and highway authorities.
Hit the post button too soon.
I was going to re-emphisize that full pipeline pressure can be felt by soil near a hole.  If one looks at the equation for flow across across a nozzle, valve or hole, approximated by, Q = Cv * (Pi^2 -Po^2),
Pi = pressure inside pipeline
Po = " outside
you can see that when the flow is very small, as it is when it is just starting to develop and leave the pipeline through a new hole, the pressure drop from inside to outside = apx. 0, so full pipeline pressure is there.  When flow through the leak reaches sonic velocity, both flow and the pressure drop across the hole are at maximums and you have the conditions to determine maximum flowrate possible from the leak.
So, IMO its very difficult for soil to stop a pipeline leak.  On one hand maximum acceleration pressure will push a grain out of the way; on the other, it must resist full momentum from a maximum flow velocity.  Energy (pressure head or velocity head) cannot be created or destroyed by soil trying to resist a pipeline leak flow.  The only way soil grains have to reduce the total energy head is by providing friction to the flow, which would require very high cohesion between individual grains.
<OK, now hit post button>
Simple physics can apply to calculate maximum theoretical flow. dP=1/2 * rho * v^2
v= (2*dP / rho)^2
Q=A*v=9 gpm
In a short time of beginning of leakage, soil adhered to the pipe will be broken. It may be less than 1 second or so. Negligible. Once it happens, soil resistence will be zero and then only resistence will be the liquid back pressure formed by the diesel spilled. It will take long time and can't be higher than 3 ft head, so again not significant. Friction loss at the opening can be more significant, but not very big. My ball park guess is 10 to 50%.
Kyong, what does rho represent?
I get 5.6 gpm, because kyong forgot the vena contracta area ratio of flow through a square edged hole which is 0.62, so Flowrate = 9.06 gpm * 0.62 vena contracta area ratio = 5.62 gpm.
192 bbls/day
Only some $14,000 a day if it was today's market crude oil. Price for diesel is on your local gas station pumps.  Its a lot higher here I'm sure.
Antwerp, rho is density.
BigInch, your vena contracta factor 0.62 is more specific than my 10~50% friction loss.
One thing I reconsider is that resitence by liquid can be bigger than I originally thought. If ratio of compactness of the soil to leakage flow rate is high, it can be prettry significant, because liquid need to penetrate the soil.
Soil in a trench is no factor at all.  Nobody in the petroleum pipeline business considers any such doil resistance.  Trenches are full of sufficient voids.
Besides, whenever fluid is stopped in its path leading back to the hole, pipeline pressure catches up to it.  Full pressure can be transmitted through the tinest hole provided that there is (effectively) no flow.  Your equation predicts the same effect.  What is pressure DROP when V = 0?
http://virtualpipeline.spaces.msn.com
There are engineering disciplines that do not ignore for conservatism or simplification the fact there is resistance to flow in porous media.  Think of fluid flow in soil as occurring in many pipes of very small diameter.  There are many earthen dams that retain water without blowing out thanks to this phenomenum.
As long as there is some flow, there is a pressure drop that can be calculated, so full hydrostatic pressure behind the dam will not be seen at that point where the pressure is being calculated.  Without flow, pressure drop = 0.
Just remember the Donald Duck cartoon.  The dam doesn't blow, until he puts his finger in the little hole.