Does anyone have any references for headed studs in masonry? ACI 530-02 (2.1.4.2.3) does not address headed studs loaded in a group. How do you handle this?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Embedded headed studs in masonry
|
RE: Embedded headed studs in masonry
It would be interesting to calculate a stud group in masonry and the same stud group with the same boundary condition in concrete with ACI 318-02, Appendix D voodoo equations. My guess is that that the masonry numbers would be higher!
RE: Embedded headed studs in masonry
2-3 & 2-4.
RE: Embedded headed studs in masonry
For shear (Bv), there is no reduction for spacing of bolts per '03 IBC. You still need to consider edge distance. You used to have to take a reduction per '94 UBC for spacings less than 8db (UBC 2107.1.5.3). Why the gurus changed this, I do not know. This is not intuitive and I share your confusion.
There are, however, very few instances where an embedded connection with multiple studs is subjected to pure shear. I can usually draw a FBD that puts a stud row in tension.