How do fused disconnects get a Horsepower rating?

I have a squared fused disconnect (600V, 60A, c/w 60A fuses)...it has a rating of 30HP on the box from the manufacturer...

Any Idea...

Regards,
TULUM

RE: HP RATING

You have to use dual element fuses, or time delay fuses.  
respectfully

RE: HP RATING

(OP)
Not sure I get you...

So because the fuses (in this case AJT60) is time delay it better protects motor loads...not sure though how 30HP is the magic number?

Regards,
TULUM

RE: HP RATING

I may have misunderstood your question.
Unless the switch is rated at 100%, it will be suitable for 48 amps, continuous current, under CEC. That is probably insuficient for a 50 hp. motor, particularly when you add the extra 25% ampacity required for motor circuits..
I thought you were wondering how you could start a 30 hp. motor on a 60 amp switch. You can't with the normal fuses.
respectfully

RE: HP RATING

In general, I believe that fused switches get a horsepower rating by design and test to CSA or UL standards. That would include sizing to CEC and NEC code requirements for continuous current plus code and/or agency requirements for starting currents and interrupting load (locked rotor?) current.

RE: HP RATING

Refer to NEMA KS-1 - this is available for download at www.nema.org.

The horsepower rating is defined differently for fused and non-fused disconnects.

For fused disconnects, it's the largest horsepower that can be started using standard fuses sized at the disconnect switch max current rating.  There's a "standard" horsepower rating that applies to any type of fuse and a "maximum" horsepower that applies to time-delay fuses.  

In the US, any disconnect sw used as a motor disconnect must be "horsepower rated", but I've never seen one that wasn't, so it doesn't seem to mean much in reality.  

RE: HP RATING

(OP)
Thanks for the tips guys...

I will look into th download

Regards,
TULUM

RE: HP RATING

Notwithstanding the fuse issue mentioned by dpc which can serve to lower a HP rating of a fused vs non-fused disconnect, disconnect switch maximum HP ratings have to do with inductive load breaking capacity, the ability of the switch to interrupt locked rotor current safely as mentioned by CJCPE. Maximum current load capacity is based on resistive loads.

Eng-Tips: Help for your job, not for your homework  Read FAQ731-376

RE: HP RATING

What jraef said..

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources