What is the correct method for grounding and fusing control transformers for the European market? Must one leg of a 220V control xfmr always be grounded?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
European Control Transformer Grounding
|
RE: European Control Transformer Grounding
RE: European Control Transformer Grounding
For a single secondary winding, single voltage ransformer, ground one end of the winding.
In NEMA land, for a single secondary, centertapped winding, ground the center tap.
For a multiple tapped, multiple voltage winding, ground the "0" volt tap. this may or may not be a neutral.
For a transformer with multiple secondary windings, ground each winding on it's own merits. Be aware that a seperate winding may be provided for a circuit that a designer specifically wants to isolate from ground.
Be aware that while the grounded circuit conductor and the neutral conductor are often the same conductor, there may be exceptions.
The final authority is the code or practice in the country of intended use.