Hi all, could anyone tell me what the test terminals on a window-type Current Transformer are intended for: what type of "tests" might we use them for?

Richard Byrne, E.E.T.

RE: CT terminals

Turns ratio (TTR)

RE: CT terminals

rbyrne15,
These terminals are used for a modified primary injection test.  An example would be 100:5:5 ratio - (primary:secondary:test). A small test current is injected into the 5 ampere test winding.  A replica current is generated in the 5 ampere CT secondary winding which is then fed to the protective relays.  You can now test the circuitry without the high currents/high voltages associated with primary injection testing.
Raisinbran

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources