Hi all, could anyone tell me what the test terminals on a window-type Current Transformer are intended for: what type of "tests" might we use them for?
Richard Byrne, E.E.T.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: CT terminals
RE: CT terminals
These terminals are used for a modified primary injection test. An example would be 100:5:5 ratio - (primary:secondary:test). A small test current is injected into the 5 ampere test winding. A replica current is generated in the 5 ampere CT secondary winding which is then fed to the protective relays. You can now test the circuitry without the high currents/high voltages associated with primary injection testing.
Raisinbran