Transformer 2000KVA 10KV/B2

Transformer 2000KVA 10KV/B2

Transformer 2000KVA 10KV/B2

(OP)
I have to order for distribution transformer 2MVA
what is the main data that I should indicate in the inquiry
what is the main tests and certificate that supplier should provide for the transformers

thank you for your help

freind from TUNISIA

RE: Transformer 2000KVA 10KV/B2

Is it a substation type, or padmounted type?  What are the primary and secondary voltages required?  Self-cooled (OA), or fan-cooled (FA)?

To begin with, you should require it meet current ANSI C57 specs., and require power factor, partial discharge, impulse, and gas-in-oil tests.  

We typically require the primary (high-side) be delta-connected, with the secondary (low-side) be grounded WYE connected.

The BIL (lightning) levels are determined by the system primary and secondary voltages, and are provided for in ANSI C57.

Lastly, have you made any determination as to energy loss requirements (how energy efficient do you want it to be?)
Typically, the more energy efficient, the higher the asking price.  The winning bid will have the cheapest of: asking price + 30-year energy losses.

RE: Transformer 2000KVA 10KV/B2

If it's 10 kV, it is probably IEC not ANSI.

RE: Transformer 2000KVA 10KV/B2

jghrist: You're right-on.  That had crossed my mind.
At any rate, he's got a bit of reading to do.  Maybe someone in Europe can forward him a copy of their specs. to get him going quickly, once he can be more specific as to system voltages.

RE: Transformer 2000KVA 10KV/B2

Good morning Gentlemen
I’d like to remind everybody about top location of the primary and secondary bushings for IEC performance  of the Transformer 10 kV. This could effect to layout .

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources