Hi everybody

I am designing a foundation for a machinery which transmit an important torsion in addition to other moments, horizontal and vertical foces.
The foundation consists of a rectangular concrete slab.

My question is how to calculate the shear force produced by the torsion, in order to calculate global the slip safety factor whith the other horizontal forces.

I have seen similar calculations which transform the torsion into a shear distribution on the slab-ground interface and then integrate it into an effective shear force which is possible to combine with the horizontal forces.

Unfortunately I don“t know such formulation.
Maybe someone knows it.

Thanks
Ruben

RE: Motor torque transmited to ground

Let's set the planar coordinates first, so I can keep what I'm telling you straight!

Consider your computer screen to be the X-Y plane.  The Z axis would then go in to the screen.

I assume you are considering a torsion in the X-Z plane, or one that is trying to spin your foundation against the soil.  You can compute the friction interface as a result of a couple to replace the torsion (moment).  For instance if your torsion is 1000 ft-lbs and your preliminary foundation size is estimated to be 8'x6', with the short side oriented along the X axis (conservative approach) , then you would replace the torsion with a couple at 1/3 in each direction on the X axis or having a separation of 2 feet.  Thus your force would be 500 lb in the Z direction at X=1' and 500 lb in the -Z direction at X=-1'.

Nothing magic about the 1/3, other than I consider that foundations are generally more heavily loaded near their centers and less so on the edges, thus a triangular load distribution.  You could use 1/2 instead of 1/3 and be justified as well (average force on the area).

I would suggest that you get a geotechnical engineer and a structural engineer involved, since this is not a minor foundation consideration.  You have soil dynamics and structural dynamics to consider.  I offered the simplistic approach in direct response to your question for your edification, not for you to base your design upon.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources