Electrical Panel
Electrical Panel
(OP)
I received an RFI from an electrical contractor regarding problems with an electrical panel. They are having problems terminating the feeder cables for a panel (120/208v,3phase,4wire, with a 225 Main Circuit Breaker). The cables are too large and the panel or the main circuit breaker cannot be modified to accomodate them. The panel is being fed through a 112.5kva transformer from another panel. The feeder is 4-600kcmil AWG and 1-#4/0 AWG Gnd. in 3.5" EMT conduit. I believe the sizing is correct.
I was told by a senior electrical engineer that he has never heard of any such problems like this during construction. Any advice/ideas as to why the feeder will not fit into the main breaker would be helpful.Is it simply that the panel that is being used is not capable of such a large feeder size? Thank you!
I was told by a senior electrical engineer that he has never heard of any such problems like this during construction. Any advice/ideas as to why the feeder will not fit into the main breaker would be helpful.Is it simply that the panel that is being used is not capable of such a large feeder size? Thank you!






RE: Electrical Panel
I would not expect a 225 amp breaker to accomodate larger wire.
I would normally expect copper cable rated at either 75C or 90C. for 225 amps that would be #4/0.
In your case I suggest exploring methods of installing 4/0 pigtails or pigtails that will fit in the breaker, on the end of the 600 MCM conductors.
reference CEC.
respectfully
RE: Electrical Panel
RE: Electrical Panel
Voltage drop or high ambient perhaps? He made no mention of the distance, that is often a challenge. Also we don't kow the ambient derating factor (if any) that may have required him to derate. He also didn't specify if the cable was 60, 75 or 90 degree rated, or the conductor material. For all we know he has Aluminum conductors, type THW 75deg insulation in a 55deg. C environment.
Termination companies make crimp-on "pins" just for that purpose by the way.
Eng-Tips: Help for your job, not for your homework Read FAQ731-376
RE: Electrical Panel
Sometimes this happens when conductors are increased in size to minimize voltage drops in long runs or to allow for future capacity expansion. There are a lot of legitimate reasons.
I would contact the breaker and/or panelboard manufacturer and see if they have any options to offer. If not, you will need to use an approved fitting to create a pigtail that is small enough to get into the lug kits that you have - if you have enough room.
RE: Electrical Panel
Mike
RE: Electrical Panel
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
RE: Electrical Panel
RE: Electrical Panel
Don't leave us hanging, why DID you oversize the cable like that? Curious minds want to know.
RE: Electrical Panel
https
Mike
RE: Electrical Panel
RE: Electrical Panel
Thanks for your advice everyone! I really appreciate it.
RE: Electrical Panel
Eng-Tips: Help for your job, not for your homework Read FAQ731-376
RE: Electrical Panel
225A panel and 75 kVA transformer or 400A panel and 112.5kVA tranformer but not the mix-match. The designer should make up his mind (correctly).
225A panel is only good for 180A which is 65 kVA. If this is adequate then pick a 75 kVA transformer and a 225A panel.
If he/she feels 75kVA is not good and picked 112.5 kVA. It makes sense to pick a panel to permit full use of the 112.5kVA (or 311A) and a 400A panel makes most sense.
The design as stated in the original post is inconsistent or indecisive.