Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Donate Today!

Do you enjoy these
technical forums?
Donate Today! Click Here

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

cvirgil (Electrical) (OP)
31 May 06 10:55
What is the difference between the two?
dpc (Electrical)
31 May 06 11:40
"Residual" method involves putting a relay element in the neutral (common) leg of three individual phase CTs in a wye connection.  Any residual current flowing in the neutral of the wye represents ground (and/or) neutral current.

Zero sequence is also known as flux summation and involves putting a  window-type CT around all three phase conductors.  Normally, the flux of the three phase conductors should sum to zero so there will be no current in the CT secondary.  If there is a ground fault, phase currents are not balanced, flux is not zero and there is secondary current in the CT proportional to the primary ground current.  
jghrist (Electrical)
31 May 06 12:51
Zero-sequence could also mean a calculated zero-sequence quantity from the phase currents.  Schweitzer distinguishes these two by using Neutral Ground for current in the CT neutral (IN channel) and Residual Ground for a calculated 3I0 current.
RalphChristie (Electrical)
31 May 06 13:28


You can obtain a much lower setting with a sensitive ground fault protection (zero sequence ground fault protection) than with residual ground fault protection.
A setting of 1%-2%  Full Load Current is obtainable with sensitive ground fault protection while a setting of lower than 10% Full Load Current (residual ground fault protection) normally result in nuisance trips.

For additional info see also the NPAG, chapter 9, "Overcurrent protection for phase and earth faults"
http://www.areva-td.com/servlet/ContentServer?pagename=TDE/AGF_Product/Product_Detail&;c=AGF_Product&cid=1089880316992&;amp;rid=&lid=en&pid=1017999014820&tab=Chapters&id=1056536208254

Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon

Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close