Install shell tube exchanger vertical
Install shell tube exchanger vertical
(OP)
Is it possible to install all shell and tube exchangers vertical. To save space I would like to mount 3 exchangers (1x CEP, 1x AEM, 1x BEV) vertical instead of horizontal.
I noticed that the drain and vent nozzles have a wrong location. But is it mechanically possible? What are other points I have to look after?
I noticed that the drain and vent nozzles have a wrong location. But is it mechanically possible? What are other points I have to look after?





RE: Install shell tube exchanger vertical
It is the shell side that is most effected. There are baffles in the shell that direct the fluid in certain directions, and prevent pooling if it is steam. These would necessarily change when in the vertical position, as well as the placement for the inlet, outlet and vents.
So, bottom line is yes shell and tubes can be vertical but they must be made that way.
RE: Install shell tube exchanger vertical
RE: Install shell tube exchanger vertical
rmw
RE: Install shell tube exchanger vertical
Their are some very important caveats on the design and operation of such exchangers.
The majority of our exchangers (approximately 100) are vertical.
RE: Install shell tube exchanger vertical
More information...please...What are your liquids ?
If the heat exchangers are equipped with saddles, are the saddles designed for gravity in the new configuration ?
As a general rule of thumb, if the heat exchangers are liquid to liquid, you can probably get away with it...
However, if there is phase change(evaporation or condensation) the answer is probably no....
Maintenance access and tube replacement are other issues for you to consider
RE: Install shell tube exchanger vertical