CT turns ratio

CT turns ratio

CT turns ratio

(OP)
Gidday All,
I fiddle with microamps all day, my only contact with real mens'business (mega-amps), is when I go to the scrap metal yard, for a bit of dumpster-diving, and I sometimes can touch those real 3000 amp copper bus-bars, and SCR's the size of dinner plates that youse guys play with all day.
Any way I picked up this CT, actually it is 3 CT's potted.
The nameplate reads:-
   PURPOSE       MET
   GROUP
   FREQ.         50~
   CLASS         C  
   ON RATIO      100/5
   SPEC          ASC45
   MAG CURRENT
   RATING        7.5 VA
   OCF  230 for 3 SEC
   PRIM TURNS    2
   SEC TURNS     39and a half
   RATIO         5/100
   SYSTEM VOLTAGE 415

So, what is OCF, and why do they tell me that the sec turns is 39 and a half?
Regards,  Ray.

RE: CT turns ratio

The turns ratio of the transformer tells you how the current is going to be changed. The ratio of 100/5 is the nominal turns ratio.
On large power bushing type transformers the primary turn is one.  So for a ratio of 100 to 5 or 20 to 1 the secondary would need to have 20 turns.
This say when you have 100 amps flowing in the primary turn then you would have primary current times the turns ratio flowing in the secondary of the ct. turns ratio is 5/100 or 1/20 so 100amps *1/20 = 5 amps secondary.

now in your transformer there are 2 turns in the primary and 39.5 turns in the secondary for a ratio of 2/39.5 = 1/19.75 which is almost 1/20

So if you have 100 amps flowing in the primary of your ct.
you will hve 100*1/19.75 = 5.063 amps secondary.

It is nice that they told your exact turns ratio.  that way you dont have to perform a ttr to determine the exact ratio.

Hope this wasn't too simplistic and that it helped.

RE: CT turns ratio

OCF ? Over-current F... something

May be the max current the CT is able to sustain for 3 sec
before it is permently damage. Other ideas?

RE: CT turns ratio

Probably OverCurrent Factor, meaning it will sustain 230 times nominal for 3 seconds.  

RE: CT turns ratio

(OP)
Thankyou for your replies, Gentlemen.
 The thing that intrigues me, is how do they get that one half turn, assuming that the CT is a toroid.
I might have to saw this thing open to satisfy my curiosity!

Regards.

RE: CT turns ratio

A half turn would seem easier than a full turn if both ends of the secondary winding exit from the same side of the core.

RE: CT turns ratio

The simplest way to obtain 1/2 turn compensation in a toroidal CT is by winding 2 wires in hand (parallel) which, in this case is 40 T.  Drop 1 turn on the compensating winding leaving 40T & 39T. If you take the average of that it is 39-1/2T.  There are other ways but this, as I say, is the easiest.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources