presurization of main stairs¦ building

presurization of main stairs¦ building

presurization of main stairs¦ building

(OP)
Hello

  I need to select a fan to presurize a 21 floors bulding´stairs. Which parameter will determine de cfm required for this porpuse? the building is located in Dominican Republic.

Thanks.

RE: presurization of main stairs¦ building

First you need to know the volume of the stairwell so air changes per hour may be calculated.

Then you need to know tha pressure you want to maintain in the stairwell which will be influenced by the openings to the stairwell.

RE: presurization of main stairs¦ building

(OP)
ok the volume of the stairwell is 1,100 m3. Which criteria will determine the air changes? and how do i know the pressure i need to maintain

RE: presurization of main stairs¦ building

I am relatively new, but from my TAB days I think in a stairwell you want 2-3 air changes per hour. The pressure is determined by the pressure on each floor. Are there floors where a positive pressure is required? Or vice versa?

RE: presurization of main stairs¦ building

If you were to go by BS 5588-4,

It would be something like this:

With 3 doors fully open(floor on which fire is on+floor just below+exit door)and all other doors fully shut,an air velocity of 2m/s should be achieved across the door area.

Assuming 2.1mx1m doors,

required air flow= 3x(2.1x1m2)x 2m/s=12.6 m3/s

You must add a safety margin for leakage from ducts,doors on other floors,wind effect etc.I have used figures as high as 1.25.

When all doors are closed,a pressure differential of 50 pa must be achieved between the stairwell and the corridor.The force that needs to be exerted at the door handle should not exceed more 100N.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources