×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

3-wire Induction Generator Connection

3-wire Induction Generator Connection

3-wire Induction Generator Connection

(OP)
I am working with an application where an individual is planning to connect a 256 kW, 600 volt three phase induction generator to the utility grid via a 600/4160 volt step up transformer. The transformer installed is HV wye - LV delta and the desire is to install a 3 conductor armoured 5kV cable for the utility connection. The utility is considering the need for a neutral connection to the transformer wye point (i.e. 4 conductor cable) but I believe the wye connection could be left ungrounded in this case as the induction generator would simply provide balanced 3-phase power to the grid and could never operate islanded without any excitation. Single phase loads would be serviced by the utility side 4-wire distribution transformer connected to the 4160 volt system. Does anyone see any problems with this scenario?

RE: 3-wire Induction Generator Connection

Hi kmh1
My experience is with three single phase transformers rather than one three phase transformer.
If the primary neutral is connected to the system neutral in a Wye Delta bank there are some serious issues with primary voltage unbalance and primary phase loss.
The utility may require the ground/neutral to be run with the phase conductors as a grounding conductor but it must not be connected to the transformer primary neutral with a delta secondary.
If the primary looses a phase, the remaining energised phases operate as open delta. The third transformer will have it's secondary energized by the connection to the open delta. The primary that has lost power will backfeed the lost phase to the point at which the phase has been interupted.
This creates a serious hazard to utility service crews, and, depending on the ratio of the load and the capacity of the transformer, can result in other equipment being destroyed by low voltage and/or overheating and eventual failure of your transformer.
For the wye/delta connection to avoid these issues, the utility must protect against phase loss and maintain the primary voltages equal within a small part of 1%. The actual figure must be a small part of the percent impedance of the transformer(s). Most utilities float the neutral. I know (and have had issues with) several utilities who connect the primary neutral and burn up a lot of transformers and a lot of refrigerators and freezers belonging to subscribers.
good luck
respectfully

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources