when you remove chilled water from the system to drain a line to do a repair, how do you refill the system?

RE: chiller makeup water?

There should be a make up/fill valve somewhere in the system.  I've seen both auto fill and manual fill set ups.

If you have chemically treated water or glycol systems even the auto fill valves are valved off, so you know when you dilute the system.  If you have a substance in the system that needs to remain at the right concentration, you don't want leaks in the system to cause uncontrolled dilution.

If you can find the systems expansion tanks or air separator, the fill valve should be in that area.

RE: chiller makeup water?

If you dont know where are or is the make/up valve, you can conect hose water in the the lower point of system lop.  

Open one valve in the higuest point of that piping lop (to vent the air from the system when the system is charged with water) then open slowly the hose valve with continuos verifycation in vent valve.  After only water flow with no air bubles close valves and start the water pumps (not the chiller) Now verify again if the system is full of water in the ventilation valve for air traped or low water level.

if yes repeat the procedure

Pastor

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources