(OP)
For those of you who do Short Circuit Studies, what is the current thinking in considering cable limiter lugs installed by the utility on their transformers?  Should the study be done with taking into account any current limiting ability for a worst-case condition?  Is there anything written on including or excluding limiter lugs in studies? Thanks

RE: Cable Limiter Lugs

Cable limiters should not be counted on as a means of reducing downstream fault currents.  The limiters are intended as cable protection for the individual conductors in parallel.  From that stand point, ideally the limiters would not operate for any fault downstream of the cables.  Even if the limiters did open that portion of the system, I've never seen a series rating where cable limiters were the part of the listing.

RE: Cable Limiter Lugs

(OP)
David,
That was the answer i was looking for.  Thanks

RE: Cable Limiter Lugs

Quote:


CABLE LIMITER APPLICATIONS
*  Service entrance conductors
*  Between transformer or network bus and busway
terminal boxes
*  Large feeders with three or more conductors per phase.

LIMITER FEATURES
 Current-limiting characteristics provide protection to
conductor insulation and reduce damage when faults occur.
 Properly applied cable limiters may permit the use of
equipment with reduced withstand ratings

See the enclose link for additional information.

http://www.bussmann.com/library/bifs/1042.pdf

RE: Cable Limiter Lugs

(OP)
So Cuky, you say that they are suitable for current-limiting to downstream panels, enough to lower the rating of those panles below the available SC current witout the limiters?  That seems to be in contradiction with DavidBeach.

RE: Cable Limiter Lugs

Dumbo2929, it is possible that the limiters will, mathematically, limit downstream fault currents in specific applications, but as far as I know you will not find a listed series rating that includes cable limiters.  Without that listing, the mathematical reduction in fault current won't let you reduce the rating of any of your downstream equipment.

RE: Cable Limiter Lugs

Even though current limiting fuses and limiters have different characteristic to respond to short circuit, still they have some similarity in term of limiting fault current as described in the following example:

*    Limiters protect cable by “limiting” the thermal damage of the cables insulation under fault conditions.
*     In spot network transformers, limiters often coordinate with the secondary fuse.
*   Their current-limiting feature can be used to minimize arc flash hazards by reducing the magnitude of the arc flash current and the time of the arc flash exposure according with Copper/Bussmann publication.

For coordination purposes, see a sample of TC characteristics curve below and the let through current in the previous link

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources