dryer vent pipe length

dryer vent pipe length

dryer vent pipe length

(OP)
Single Load Stack Dryer
Mechanical non-coin operated
Maytag model MLE19PN (could be MLB19PN)

According to manufacturer's data we can install a 4" vent pipe to 65 feet with no 90 degree turns.  We have 3 90 degree elbows. With that the length comes down to 28 feet.

We need to go 10 feet in vertical to ceiling and then another 50 feet horizontal to the outside.

Can we go to a 6 or a 8 inch vent or use some fan  or special elbows so that we can go 60 feet?

Two of the turns are inside the building and once its outside we are counting that as the third elbow. If there is a louvre there, does that count as the third elbow?

RE: dryer vent pipe length

exhausto makes dryer venting systems

RE: dryer vent pipe length

(OP)
We just have one dryer. Is there something light duty?
(residential type)

RE: dryer vent pipe length

It will be wayyyyyy more helpful to ask the dryer manufacturer if he will give you a fan curve for the fan or tabulated fan capacities, ie, static pressure vs cfm.

Then you can vary the ductwork any way you want.

RE: dryer vent pipe length

(OP)
http://www.designmep.com/designmep_009.htm

manuf data does not show fan curve just length on a 2-1/2" vent pipe and a 4" vent pipe.  Something like above calc would help if someone has installation at 60 ft -- found it on web.

RE: dryer vent pipe length

As I see from your codes tables, 5" duct has 3 times lower pressure drop per linear feet then 4" duct, so you shouldn't have any  trouble using it for your lengt.

sunshine

RE: dryer vent pipe length

Watch your velocity...
Dryer vent is sized to convey the lint, not on a pressure drop of the air. Flex is a no-no for anything other than connecting.
As with kitchen exh systems, the grease/lint needs motivation or the duct fills up.
The lint will build up & issues will arise, not the least being fire...
Ask the code officials as I've run into some states &/or cities that don't allow booster fans.

Issues with upsizing duct must be addressed.

good luck
slj

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources