Please let me know the type of cable to be selected for a 11KV system (incoming / outgoing cables to/from a 11kV switchboard) is 6.35/11KV grade or 11/11kV Grade?

Transformer on the upstream side (132/11kV) is high resistance grounded.

RE: Voltage grade of cables

Since the transformer on the upstream side (132/11kV) is high resistance grounded, you need to have same precautions as when the network 11kV were isolated. Hence, you must use 11kV/11KV grade cables.

On the other hand, for medium voltage systems above 5kV, the Insulated Power Cable Engineers Association (IPCEA) have requirements in which conductor insulation thickness for a particular voltage is determined by the length of time that a phase-to-ground fault is allowed to persist. Three thickness sizes are specified and are related by the terms 100%, 133% and 173% levels to be applied as follows:
a) 100% level, where the clearing time will not exceed 1 minute.
b) 133% level, where the clearing time exceeds 1 minute, but does not exceed 1 hour.
c) 173% level, where the clearing time exceeds 1 hour.

Obviously the 100% level can be used on any system whether solidly or resistance grounded, providing phase-to-ground faults are cleared in the specified time. This will almost inevitably require fault relaying.
The 133% and 173% levels will apply mainly to ungrounded and high resistance grounded systems, since other forms of grounding will most probably involve ground fault currents that could not be tolerated even for the time permitted. Selection between the 133% and 173% level of insulation will be determined by the time required, after
identification of the faulted feeder, to perform an orderly shutdown of the process being served.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources