Heat tracing in Argentina

Heat tracing in Argentina

Heat tracing in Argentina

(OP)
We are planning on putting electrical heat tracing on liquid lines on a peice of equipement that is destine for Argentina. The voltage and frequency of the power in Argentina is 220V, 50 Hz. Normally we use 110V and of course 60 HZ. We have access and will use the 220V rated Heat trace cable but we are wondering if the 50Hz will cause a problem or if there are other things that we will have to do different for the 50 Hz.

RE: Heat tracing in Argentina

Do you have motors?
Read this FAQ: FAQ237-1224

Do you have electronics?

Heat tape won't care as long as the voltage is correct.  Do keep in mind that:

POWER = Voltage x Voltage / Resistance

This means that 240V heat tape will actually put out about 15% less heat when run at 220V  This may or may not require some changes.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources