A fellow engineer and I were discussing insulation resistance testing and he mentioned that several times he obtains an infinite reading on his instrument without the leads connected, but as soon as he connects the leads, he gets less than infinite (the leads are connected to the instruments, but not to a specimen), although still a very high reading. Does anybody knows the reason for such strange behavior?
Thanks,
MAS2006.

RE: Insulation Resistance Testing

Leakage current.

From probe, along the lead to instrument, along the other lead to other probe.

From probe along your friends arm to his other arm to the other lead.

If you're talking gigaohm range, it doesn't take much leakage current to change the measurement.

As you add more and more things in parallel the resistance goes down.  Total resistance will be lower than the lowest of all the parallel things.

If you're measuring 5 gigaohms now with only leads connected and you connect to your motor and read (after one minute) 500 megaohms, then the motor is darned close to 500 megohams and this extra resistance isn't affecting you.

If you obtain any satisfactory measurment, you needn't worry about the effects of the leads (unless you are trending), they only make the reading lower.

If you have 100 megaohms with the lead and 90 megaohms with the motor also connected and you're expecting 200 megaohms, time to troubleshoot that leakage.

I'm not sure if there might be some kind of meter zeroing device to remove the effects of that leakage current... or maybe not.

What type of instrument are we talking about?

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Insulation Resistance Testing

(OP)
Dear ElectricPete, thanks for your reply. I will discuss it with my friend. He was using an AEMC, but I don't remember the model.

MAS2006.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources