motor overloads standards
2

motor overloads standards

motor overloads standards

(OP)
I am looking for any standardized information on overloads motors should withstand relatively to their power rating.
Is there any norm or admitted standard about that ?

Thank you

RE: motor overloads standards

2
NEMA MG-1 only required rated temperature rise at rated load (or service factor rise at service factor load). That doesn't tell us anything about overload capability... except if it has a service factor... in which case the rise at service factor load is approx 10C above the normal required rise at rated load... equating roughly to a halving of insulation life.  But there is a lot more that can be said about service factor... search this forum.

The fact that NEMA also allows the standard motor to operate at a voltage up to 10% low would seem to imply to me that NEMA is suggesting motors contain at least 10% overload capability.

Motor overload protective settings for 49 device are typically in the range of 115%-125%FLA and higher for service-factor rated motors. Some info in IEEEC37.96 section 7.2.9.1.  I'm not sure exactly where these numbers originated, it may be the NEC.  

The motor purchaser can request from the manufacturer a thermal damage curve IAW IEEE620-1996 which will define exactly how much time is allowed for any given level of overload.  Alternatively if the motor is required to have a known short-time duty above rated, the user can make this part of his specification.





RE: motor overloads standards

I agree with electricpete and would only add that you should not expect any overload capability beyond what is provided by the motor's service factor and duty specifications.  

 

RE: motor overloads standards

Electricpete is on the money as always:)

I would also like to add that the report from GAMBICA for vfd's is really good as far as insulation stresses for motors including NEMA MG1 pt 31 and IEC 60034-17 (the other motor standard that I see more and more these days.)

http://www.gambica.org.uk/newsite/public.html#g1

Carl

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources