Electrical Reducing JBs

Electrical Reducing JBs

(OP)
Hi,I have big size of cable but the terminal box motor entry small. I use the reducing JB and from reduce JB one cables to the terminal box motors. unapurtunitly client asking any code/regulation permit this arrangment at site?. Help

RE: Electrical Reducing JBs

dungun

Question(s):
Motor Size (HP), Motor Supply Voltage, Supply Cable Size, What Country, and what is/does "unapurtunitly" mean?

12fish
As Iron sharpens Iron so does a man sharpen the countenance of his friends.

RE: Electrical Reducing JBs

(OP)
Hi 54494060
150KW, 440V ,300mm sq, Subcontinent, mean ... "however" client...

 

RE: Electrical Reducing JBs

Is the cable sized for volt-drop reasons, or for thermal rating? I am guess it will be volt-drop unless you have a very unusual environment - 185mm² would be about right for a typical installation. You could safely reduce the cable to a smaller size of adequate thermal rating provided that the protective devices are suitably selected for the smaller cable, unless this is specifically excluded by your local regulations. You haven't yet disclosed where you are, so that is open to speculation.

----------------------------------
  I don't suffer from insanity. I enjoy it...

RE: Electrical Reducing JBs

(OP)
ScottuUK
This size due to the voltageDrop. All the sizing done by properl calc i.e from MCC to red JB and from JB to motor. All Jbs/acessories according to area clasification. No Govement regulation restriction but I dont find any restriction in code too (may be overlook) if someone experience the same thing can be shared. From northen pakistan.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources